- This topic has 6 replies, 4 voices, and was last updated 8 years, 10 months ago by bpietrewicz.
-
AuthorPosts
-
-
February 8, 2016 at 12:19 pm #76nssabolKeymaster
UNM Data Center and Server Room Standard
Attachments:
-
February 11, 2016 at 1:29 pm #95dbanwardParticipant
Hello,
I am the Sys Admin for UNM Press. We are probably a tier 1, unless we combine our 2 locations, which has been the case in the past, then we would be a tier 2 facility. I have some questions and concerns on this draft.
1. power tap – is this a wall tap? If so, this could be defined as nothing more than an outlet splitter (making one outlet into three outlets, and such). If you mean power strip, same thing. Maybe you are referring to a surge protector, but it notes that surge suppressors should not be used. Can you be more specific? The exact specifications will be useful.
2. In the Standard Specifications section, Section 1 – this refers to Appendix A, but in the definitions of tiers these contradict. For example Tier 1 section states, “The Facility meets minimum requirement for the safe operation and maintenance of computing equipment and protection of assets. Door lock, power tap, UPS recommended.”
But in the chart (Appendix A), there are more requirements such as having an emergency shut off, having UPS (is required and not recommended), building and door security system, more. What are we to follow the chart or the tier classification if they do not match?
3. Continuing on with the requirements for Tier 1. The first few sections about fire alarms, suppression systems, and emergency cut-off systems you refer to national, state, and local building codes. After looking into the City of Albuquerque building code, which refers to the International Building Codes (IBC) from 2009, I have come to the conclusion that these are not requirements at all for my main campus location. We do not even have smoke detectors in that location, and after looking through IBC I can see that UNM can justify us not having one. Question is, if it is a requirement what is the specific policies you are referring to?
Thank you for your help, and thank you for putting this together. I understand the need for it and will work towards compliance when this is official.
Also is there a better way an organization like mine can get word about this document and process besides checking this page every so often? Maybe a message to the IT email list?
Darrell Banward
System Administrator, UNM Press
277-0978
-
February 11, 2016 at 1:33 pm #96dbanwardParticipant
I forgot to ask if building security alarms (alarms set at night for entire building) cover the requirement or are the security alarms supposed to be specific to the data center/server room separate from the building alarm?
-
February 15, 2016 at 10:05 am #184bpietrewiczKeymaster
Darrell,
Thanks for taking the time to comment.
1. Per the standards the State Fire Marshal uses when inspecting UNM buildings, a UL labelled POWER TAP OR RELOCATABLE POWER TAP is required because it will trip if the overload is on either side of its circuit. A surge protector will only trip with an overload on one side of its circuit. Power taps and surge protectors are very similar with the exception noted above and cost about the same.
2. Section one is meant to be descriptive of the tier. The appendix is specific to the requirements. Appendix A is intended to be more specific on how a department accomplishes what it has chosen from some of the “recommended” areas in the Tier 1 section. An example would be if a department elects to forgo the UPS that is recommended in Tier 1 (along with all attached liability for such a decision), then none of the specific requirements for a UPS in Appendix A are applicable. Alternately, if a department elects to have a UPS (as recommended in Tier 1) then said UPS must meet the required specifications outlined in Appendix A, and considerations may additionally be given to the recommendations of Appendix A.
3. Thank you for bringing our attention to use of the phrase “local building codes”, we should remove it for clarity. UNM resides under the jurisdiction of the State of New Mexico and not the City of Albuquerque. Currently the State Fire Marshal uses IBC/IFC 2003 and NFPA 72 1999. Any specific questions would be referred to them for answers, as was anticipated when the above sentence was articulated in general terms.
Regards,
Brian Pietrewicz
- This reply was modified 8 years, 10 months ago by bpietrewicz.
-
-
February 12, 2016 at 4:36 pm #176elishaParticipant
Is there a proposed timeline for compliance, and when would the Office of the CIO like any variations from the standard to be filed? Is there a standard template for filing an exception? I’m also wondering what manner of communication is preferred for confirming data center standard tier.
Under Process for Review or Update of the Standard, I’m not clear about this language:
Process documentation development
Each site will have policies defining roles, responsibilities, and performance standards
Each site change will require a review and update of all documentation
Site Books will be developed for each site covering all tasks and responsibilities required to support that site. This will include all policies, site standards, and procedures”
Does site refer to a Server Room or Department? This would make sense to me, but I couldn’t tell if it was referring to a service owner responsibility or a process for refining this document.
- This reply was modified 8 years, 10 months ago by elisha.
-
February 15, 2016 at 10:38 am #186bpietrewiczKeymaster
Elisha,
Thanks for taking the time to comment.
<p style=”background-image: initial; background-attachment: initial; background-size: initial; background-origin: initial; background-clip: initial; background-position: initial; background-repeat: initial;”><span style=”font-family: ‘Calibri’,sans-serif; color: black;”>Internal Audit will use the DC Standards to conduct their review of data centers (as with UNM IT DCs). In addition, we would expect management of the distributed IT organizations to manage to the standards (as minimums). Finally, if requested by the administration, UNM IT would check for compliance and inform management.</span></p>
<p style=”background-image: initial; background-attachment: initial; background-size: initial; background-origin: initial; background-clip: initial; background-position: initial; background-repeat: initial;”>Regards,</p>
<p style=”background-image: initial; background-attachment: initial; background-size: initial; background-origin: initial; background-clip: initial; background-position: initial; background-repeat: initial;”>Brian Pietrewicz</p>
-
February 22, 2016 at 8:39 am #275bpietrewiczKeymaster
Sorry about the post above. Here’s a clean version.
Internal Audit will use the DC Standards to conduct their review of data centers (as with UNM IT DCs). In addition, we would expect management of the distributed IT organizations to manage to the standards (as minimums). Finally, if requested by the administration, UNM IT would check for compliance and inform management.
regards,
Brian
-
-
AuthorPosts
- The topic ‘UNM Data Center and Server Room Standard’ is closed to new replies.